SEPARATING WALLS (NEW BUILDINGS) SOUNDPROOFING


2.70 Wall type 2.2 Two leaves of lightweight aggregate block with 75 mm cavity, plaster on both room faces (see Diagram 2-16)

Example of wall type 2.2

The required mass per unit area would be achieved by using:

This is an example only. See Annex A for a simplified method of calculating mass per unit area. Alternatively use manufacturer’s actual figures where these are available.

Diagram 2-16: Wall type 2.2
Diagram 2-16: Wall type 2.2 soundproofing

Additional construction: Wall type 2.3 should only be used where there is a step and/or stagger of at least 300 mm.

2.71 Wall type 2.3 Two leaves of lightweight aggregate block with 75 mm cavity and step/stagger, plasterboard on both room faces (see Diagram 2-17)

Note: The composition of the lightweight aggregate blocks contributes to the performance of this construction with a plasterboard finish. Using denser blocks may not give an equivalent performance.

Example of wall type 2.3

The required mass per unit area would be achieved by using

This is an example only. See Annex A for a simplified method of calculating mass per unit area. Alternatively use manufacturer’s actual figures where these are available.

Note: Increasing the size of the step or stagger in the separating wall tends to increase the airborne sound insulation

Diagram 2-17: Wall type 2.3
Diagram 2-17: Wall type 2.3 soundproofing

Resistance to the passage of sound 25