Nature of Proposed Amendment

  1. In an attempt to determine the likely technical and financial impact of the proposed new test methods for fire resistance and reaction to fire the then DETR helped to sponsor two research projects4,5 led by Warrington Fire Research Centre. The research was steered by an Industry Advisory Group, which had representatives from industry who have experience in manufacturing all types of construction products.

Fire resistance tests

  1. In the case of the fire resistance tests on construction products, the research showed that products tested by the European test method record test times that are, on average, some 10 to 15% shorter than for those tested by the British Standard test methods. For example, a product achieving 60 minutes under the British Standard test may only achieve 50 to 55 minutes under the European harmonised test. In many cases, this reduction would lead to the product having a lower European classification, compared with the existing classification in Approved Document B.
  2. The proposal - as recommended by the Industry Advisory Group - is to retain the existing classification system to avoid confusion and market distortion. If the periods of fire resistance recommended by Approved Document B were reduced, to reflect the stiffer European tests, this could lead to a perception that safety standards were being reduced (e.g. a product previously achieving a 60-minute fire rating, that was now only achieving 50 minutes, would be perceived as having a poorer performance even though it had not been altered). This could possibly lead to an increase in insurance premiums.
  3. Consequently, it is proposed that there is no change to any of the periods of fire resistance given in Approved Document B. The implication for the industry is that, if it wishes to test to the European test methods, it may have to adapt its products, where necessary, to meet the 10 to 15% shortfall in test times. If it did not, it could lead to significantly over-engineered products being entered into the next category down. This will have cost compliance implications for the industry, which are discussed further in Annex B.

Reaction to fire tests

  1. In the case of the reaction to fire test the situation is more complex as the European harmonised test does not mirror the British Standard test. Transposition is more difficult as the British Standard tests for "spread of flame", "fire propagation" and "non-combustibility" must be compared to a single new set of tests which has seven classes: A1, A2, B, C, D, E and F. However, on the basis of the 'back to back' fire testing where the two standard regimes were compared for a range of construction products Table 1 contains the proposed transposition for reaction to fire performance.

Table 1. Proposed transposition for reaction to fire performance

National Class

European Class

Non-combustible

A1

Limited combustibility

A2-s3,d2

0

B-s3,d2

1

C-s3,d2

3

D-s3,d2

   

Note: Euroclasses E & F are not used for the purposes of the guidance in support of the Building Regulations

Reference to guidance documents

  1. The current edition of Approved Document B contains references to documents6 which give guidance on the construction and erection of fire resisting elements which are stated to satisfy its provisions when tested against the British Standard methods. It could be argued that such 'deemed to satisfy' constructions are a barrier to trade as they favour the home industry over an imported product. As such it may be felt that such guidance could stifle the development of new materials, products or constructions that satisfy the European testing regime. However, as the Approved Document will continue to refer to our current national provisions, and it is proposed to adopt the new harmonised European system of fire tests, through the publication of an amendment document, it is felt that the existing references to such documents should remain.

4 RADAR 1 Project – Modifications required to Approved Document B following the introduction of new European fire resistance test methods on currently acceptable products and constructions. Warrington Fire Research Centre, May 2000.

5 RADAR 2 Project – Correlation of UK Reaction to Fire Classes for Building Products with Euroclasses and Guidance on Revision of Approved Document B. Warrington Fire Research Centre, May 2000.

6 Examples of such documents are: Guidelines for the construction of fire resisting structural elements (BRE Report 128, 1988) and Increasing the fire resistance of existing timber floors (BRE Digest 208, 1988).